6/9/2011 11:38 PM | |
Posts: 8946 Rating: (999) |
Please check first, if at TP170B the channel MPI is activated and the MPI adress and settings are correct! You do it at system control menue "transfer"of TP |
6/10/2011 7:25 AM | |
Joined: 3/21/2006 Last visit: 10/7/2024 Posts: 10229 Rating: (1181)
|
You need a Seriell RS232 6ES7 901-1BF00-0XA0 for Download (update operating system, project, …) and Booting (filling in the case of a missing or damaged operating system). BTW, update the Protool 6.0 to SP3 Downloads for ProTool/Lite, ProTool, ProTool/Pro V6.x. best regards, Hristo MIhalev |
6/10/2011 2:09 PM | |
Joined: 5/23/2011 Last visit: 10/6/2024 Posts: 37 Rating: (0) |
I have already activated the MPI port. |
6/10/2011 2:11 PM | |
Joined: 5/23/2011 Last visit: 10/6/2024 Posts: 37 Rating: (0) |
UMENCHO ,u mean that it is not possible to download by CP5512? |
6/10/2011 2:31 PM | |
Joined: 3/21/2006 Last visit: 10/7/2024 Posts: 10229 Rating: (1181)
|
According to Projecttransfer_V1_2_e.pdf is possible but not PC/MPI-Adapter and USB/MPI-Adapter. So, in your case should it work. Sorry, I tried only RS232 cable. Best regards, Hristo Mihalev |
6/10/2011 3:17 PM | |
Joined: 5/28/2008 Last visit: 10/12/2024 Posts: 4515 Rating: (839) |
Hello Amit_86, I think thatGodfather is using a Laptop as he told that he try to useCP 5512 So, with this communication processor, Laptop can be connected to Profibus / MPI network using normal Profibus cables and Bus connectors. |
Ayman Elotaify |
|