Hello all! As per support website information there was an update on : Update V3.0.0 (6ES7 417-4HL01-0AB0) https://support.automation.siemens.com/WW/llisapi.dll/6741018?nodeid0=24206950&func=ll&objId=24204723&objAction=csView&lang=en&siteid=cseus&aktprim=0&extranet=standard&load=treecontent I am using 6ES7 417-4HL04-0AB0. So I am wondering if anybody out there expirence the same problem. See Attachment for Diagnosebuffer. Up to the last 2 entries the EXTF indication wos on, on the Master as well as on the standby CPU. I am sure there was no fault on any of my slaves until the last 2 entries. Now all is fine. Because I have 5 more complete 417H Sytem in my project and a lot of Y - Link / DP PA slaves I don´t want to come to the point again. Cheers, Hannes AttachmentDiagnoseTrain1OK.zip (618 Downloads) |
10/2/2007 12:54 PM | |
Posts: 5822 Rating: (412) |
Hello, well, first of all I would upgrade your CPUs to the latest version of the Firmware, which is V4.0.10 this can be found at: Operating System Updates for CPU412-3H / CPU414-4H / CPU414-4H PG / CPU417-4H Choose the Version of CPU you use and update, it is really necessary. Best regards J_Bell |