Hi, Thank you for the rating, that is what me keep answering questions Do you have STEP7 already... I supose not because of the rest of your questions... Maybe it is then possible that the firm that made the installation could do something for you... If not then STEP7 V5.4 SP3.1 is the newest one, you need a MPI-card like the CP5512 or a USB-cable (is cheaper) to connect from your laptop to the CPU. With STEP7 you could look into the hardware configuration online and see what is wrong. You might also program Report System Error and then you could look with "CPU messages" and/or with a WinCC/WinCC Flexible PC/Panel which errors are there. So if you have already a panel then (if the panel is not to smal) you could use RSE. The Profibus network is a RS485 network, see the manual SIMATIC NET PROFIBUS Networks for more information. |
I hope that the answer will help, if you have still questions, don't hesitate to ask me. |
|
1/10/2008 12:06 AM | |
Posts: 3 Rating: (0) |
hi this is the file i hope you can help me and i will try not to give you eny more trouble. very very tahnk you Attachment216624-1.pdf (738 Downloads) |