1/22/2008 1:06 PM | |
Joined: 9/27/2006 Last visit: 11/14/2024 Posts: 12294 Rating: (2691) |
Hello Marko; Here is the procedure to access the diagnostics Bufferas shown in the Programing with Step 7 v. 5.4 manual: How to Locate Faults 1. Open the online window for the project with the menu command View >Online.2. Open all the stations so that the programmable modules configured in them are visible. 3. Check to see which CPU is displaying a diagnostics symbol indicating an error or fault. You can open the help page with an explanation of the diagnostics symbols using the F1 key. 4. Select the station that you want to examine. 5. Select the menu command PLC > Diagnostics/Settings > ModuleInformation… to display the module information for the CPU in this station.6. Select the menu command PLC > Diagnostics/Settings > Hardware Diagnostics to display the "quick view" with the CPU and the failed modules inthis station. The display of the quick view is set as default (menu command Option > Customize, "View" tab).7. Select a faulty module in the quick view. 8. Click the "Module Information" button to obtain the information on this module. 9. Click the "Open Station Online" button in the quick view to display the diagnostic view. The diagnostic view contains all the modules in the station in their slot order. 10. Double-click a module in the diagnostic view in order to display its module information. In this way, you can also obtain information for those modules that are not faulty and therefore not displayed in the quick view. You do not necessarily have to carry out all of the steps; you can stop as soon as you have obtained the diagnostic information you require. |