hi. I have a S7-416 2DP PLC, when I upload the user program from this PLC and open the user program, some of blocks show error "there is a stamp conflict with at least one block call". and when I open the block (FIG.1) as you can see, there is problem with "call" programs. so I delete the "call" and "end call" and the problem solved. can you please help me to avoid this problem because so many blocks are the same and removing all of "call" are taking so many time? ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 07/13/2021 11:17:23New subject after splitting |
|
This contribution was helpful to1 thankful Users |
7/15/2021 3:05 PM | |
Joined: 10/10/2005 Last visit: 10/18/2024 Posts: 1921 Rating: (136) |
Hello mpakravanan, it is possible that the PG, from which do you have downloaded in the CPU has an other STEP 7 version as the PG, in which do you have uploaded the program from the CPU. It is also possible that a optional software is missing. Check after the upload which software package is missing. Information you will find in the FAQ: "How do you check a STEP 7 project for the software packages required to edit the STEP 7 project?" The timestamp errors caused by changes to interfaces. In this case I recommend to perform the block-consistency in STEP 7 and compile the complete program again. Use in this case the FAQ for your support: How do you perform a block-consistency check following changes in the STEP 7 program? Cicero |