I would like to read 40 IO's and they are all 24V. |
Last edited by: CFormagio at: 01/31/2023 14:57:15 |
|
2/1/2023 11:51 AM | |
Joined: 4/28/2015 Last visit: 11/5/2024 Posts: 3345 Rating: (379)
|
Hi, the only thing I know to solve that without PLC is to the ET200SP MultiFieldbus interface module with respective modules for DI / AI. The MF interface module can provide data via Modbus TCP, which you could read with the IOT2050. We also have a PNDriver for the IOT2050 in the pipeline, with that you could also use standard ET200SP interface modules. But I do not know when we will release this. Best regards! |