Hello Tony from Boise You are in the HMI Panel conference so I will only answer the Panel side of the question. If you can do a Ping then you should also be able to load the HMI. Check also this: https://support.industry.siemens.com/cs/ww/en/view/88633853 Use the devices with same addresses in the extended transfer dialog not the search of compatible devices if you have trouble with the searching for accessible devices. (Panel has to be in Transfer mode with correct settings for transfer and IP)(you can also try to ping the PC from the Panel) After loading the new IP configuration to the Panel you can reach the panel only by setting your PC´s IP in the new IP range. Do not go online before you try to load the Panel (the workflow is a bit different from the one you would do with PLC) Bye Murof |