Hi, I am using logo for the first time and I am trying to create some alarms in my application that is being displayed through a KTP400 BASIC. I mapped all the IO on the HMI and I can read and write values from Logo 8.4_1. I don't understand how to write the bits of the word I need to trigger the alarms on the HMI. |
4/5/2025 3:13 AM | |
Joined: 12/18/2014 Last visit: 4/9/2025 Posts: 35066 Rating:
|
Take a look at this topic: Logo to KTP700 basic alarm display |
This contribution was helpful to
1 thankful Users |
4/7/2025 1:32 PM | |
Joined: 12/14/2024 Last visit: 4/7/2025 Posts: 8 Rating:
|
Thanks for the help! |
4/7/2025 3:02 PM | |
Joined: 12/18/2014 Last visit: 4/9/2025 Posts: 35066 Rating:
|
You made something wrong with the VM addresses. Example by VW10: 1. Alarm = V11.0 |
4/7/2025 3:32 PM | |
Joined: 12/18/2014 Last visit: 4/9/2025 Posts: 35066 Rating:
|
For better understanding: |
4/7/2025 4:20 PM | |
Joined: 12/14/2024 Last visit: 4/7/2025 Posts: 8 Rating:
|
I modified that, and it's working!! |
Last edited by: AutoGen_4189346 at: 04/07/2025 16:22:56 |
|
4/7/2025 4:57 PM | |
Joined: 12/18/2014 Last visit: 4/9/2025 Posts: 35066 Rating:
|
By me works it. See attached example ans screen video. AttachmentKTP400 (V16) Alarm.zip (7 Downloads) |