8/12/2006 10:25 AM | |
Posts: 58 Rating: (2) |
Hello What kind of DP slave you would like to communicate with? Is it active or pasive? Best regards, Andre van Gijsel |
8/12/2006 1:08 PM | |
Posts: 28 Rating: (0) |
The DP Slave is an ABB Drive, im not sure if its active or passive. What would be the difference in configuration? |
8/13/2006 7:56 PM | |
Posts: 28 Rating: (0) |
Thanks Late, Im using PCS7 V6.1 +SP1 Could you post a link to the HSP as the Siemens search engine dosn't appear to be working either [:(] |
8/14/2006 3:40 PM | |
Posts: 3149 Rating: (171)
|
Hi Lost, as far as I know no HSP is available for your current PCS7 version!! Do you use a IM 157 or just insert a IM 157 in HW-Config (and use a IM153 in reality)?? http://support.automation.siemens.com/WW/view/en/22374877 nemo |
8/14/2006 6:21 PM | |
Posts: 28 Rating: (0) |
In reality im using an IM153-2BA01-0XB0, for the HW-Config im using an IM157-0AA82-0XA0, I've attached the GSD of the downstream slave, maybe this slave is not compatible?
AttachmentRPBA01N.zip (689 Downloads) |
8/15/2006 7:30 AM | |
Posts: 3149 Rating: (171)
|
Hi, you must use IN REALITY (not just HW-Config) a IM 157! nemo |