12/10/2015 9:19 PM | |
Posts: 5225 Rating: (1194)
|
Hi Adam, So what you hoping for is to have a variable frequency pulse, also called PTO (pulse train output). There will be a limitation to the frequency to what the pump mechanism can handle. Do you have an idea to what this would be? The rate of the ON and OFF should be low enough for you to code the pulse with IEC timers. Look at https://support.industry.siemens.com/cs/ww/en/view/54647747. Alternatively you can use the motion control technology function. You use the JOG instruction to get the proper on-the-fly frequency adjustment. Is that what you were hoping to find? |