10/14/2018 8:57 PM | |
Posts: 200 Rating: (6) |
Hi Thanks for getting back so quick I want the pumps to change then run for 168 hours then change again Thanks Andrew |
10/14/2018 9:26 PM | |
Joined: 12/18/2014 Last visit: 11/2/2024 Posts: 34124 Rating: (4249)
|
Here a possible solution.
AttachmentChanging_pumps_(0BA8.Standard).zip (447 Downloads) |
This contribution was helpful to2 thankful Users |
10/14/2018 9:50 PM | |
Posts: 200 Rating: (6) |
That works really well thanks I have attached what i had in mind but not sure if correct AttachmentCircuit Diagram1.pdf (347 Downloads) |
This contribution was helpful to1 thankful Users |
10/14/2018 10:16 PM | |
Posts: 200 Rating: (6) |
sorry this was the one i meant to post but still don't think it was correct as pump one would only run for 2 mins
AttachmentCircuit Diagram1.pdf (342 Downloads) |
10/19/2018 3:52 PM | |
Posts: 200 Rating: (6) |
Hi if i wanted to have Q1 and Q2 not latch but give a short pulse output how would i achieve this. Thanks Andrew |
10/29/2018 7:16 PM | |
Posts: 51 Rating: (5) |
Hi Andrew, See my change , i used a pulse block that i set by 1 second parameter and connected to Q3 & Q4. Result that Q1 & Q2 are still all the time active and upon a change over Q3 & Q4 will pulse for a second. If this time is notr correct just adjust the parameter in the two blocks. AttachmentChanging_pumps_(0BA8.Standard) pulse output.zip (347 Downloads) |