6/16/2022 2:29 PM | |
Joined: 3/16/2022 Last visit: 5/7/2024 Posts: 1 Rating: (0) |
Anybody already a solution? I tried all the proposed solutions from this topic but nothing works. EDIT: AttachmentOpcUA Error.pdf (942 Downloads) |
Last edited by: fschilder02 at: 01/29/2024 13:39:07 |
|
4/10/2024 8:05 PM | |
Joined: 9/8/2023 Last visit: 6/5/2024 Posts: 1 Rating: (0) |
Hi Chnztrk and to everyone I've found the solution for this problem well, this worked for me and I hope it works for you too. I did what comes in the following Link: in the solution #1, I have assigned the IP address with its port # of the server opc ua server. I did this in the following tag: <name>_Configuration > Connection > ConnectionInfo > ServerUri. Before doing this, first set the "opcUaConnect" bit to FALSE, this variable is linked to the communication block "opcUaClient". Once the IP address + port # of the opc ua server is set. Enter the PLC in online mode and send it to Stop mode, then apply a MRES. Wait for the connection to re-establish, put it in RUN again and try to establish communication again with the opc ua server. To do this set the ControlingInterface_opcUaConnect variable to TRUE, the error will no longer appear in the Status variable and in the SubFunctionStatus. Anyway, if this did not work for you, there is another possible solution in this link: https://support.industry.siemens.com/cs/de/en/view/109771693 |
Last edited by: Jen_Moderator at: 04/11/2024 08:05:41Text formatting and link optimized. |
|
This contribution was helpful to1 thankful Users |