3/30/2020 9:20 PM | |
Posts: 46 Rating: (0) |
Hi, Thanks for the clear explanation. But stil i dont understand the behavior. In my project i have a 4-20mA temp sensor 0-100°c. When i folow the manual i use a analog amplifier with the mesurment range min=0 and max 1000. When i run the online simulation AI1 shows 267, my AM1 shows 84 My mA meter shows 5.28mA wich coresponds with 8°C How can i get 8.4 in stead of 84 ? Same problem on the webserver I tryd to change the scaling in the analog amplifier to min=0 and max=100, but the software refuse this setting with the remark "the mesurement range derminded by gain/offset is invalid. Used mesurement range: 1 to 105. I getting despered, can you please explane wat i have to do. ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 03/31/2020 11:20:52New subject after splitting |
|
3/30/2020 9:54 PM | |
Joined: 12/18/2014 Last visit: 9/30/2024 Posts: 33855 Rating: (4210)
|
In attachment a solution for shown the temperature on the LOGO! display with a decimal place. You cannot set decimal places with the LOGO! Web Edditor, the web server can't. AttachmentTemperature_0BA8.Standard.zip (193 Downloads) |
3/31/2020 11:04 AM | |
Posts: 46 Rating: (0) |
Hi, Thanks for the reply, in my project i dont need a decimal, but now i see 82 in stead of 8°. This is confusing for the user, is there a way to solve this ? |
3/31/2020 11:21 AM | |
Posts: 46 Rating: (0) |
i dont see the example |
3/31/2020 11:22 AM | |
Posts: 46 Rating: (0) |
i dont see the solution you made. |