3/7/2019 12:29 PM | |
Posts: 9 Rating: (0) |
Ok. Suggestions ? |
3/7/2019 2:10 PM | |
Joined: 12/18/2014 Last visit: 10/1/2024 Posts: 33857 Rating: (4210)
|
Suggestions? Yes, but only as far as the keys F1 and F2 are concerned. And the rest I can only give tips, because I do not know why you do something. I do not know the function of your program and therefore do not know why you are doing something like this. I already wrote you that you have overlaps in the VM area. This means the tag "LOGO_M5". The VD0, in which the count of the counter B001 is included, consists of the V-bits 0.0 to V3.7. So you can not V0.0 and V0.1 for the F-Keys, but only check which V-bits are not yet occupied. Overall, V-bits V0.0 to V5.7 as well as V8.0 to V13.7 have so far been occupied by VM mapping. That's why I've created the following as HMI tags for the F-keys: For F1 = "LOGO_NI1" = V14.0 For F2 = "LOGO_NI2" = V14.1 For the tags "LOGO_Mx" I do not understand the meaning and the function in the LOGO! program. Attached are the customized LOGO! program and the customized TIA project. However, the adjustments only refer to the F-keys. AttachmentCHEMICAL FILL_V2.zip (229 Downloads) |
This contribution was helpful to1 thankful Users |
3/7/2019 2:20 PM | |
Posts: 9 Rating: (0) |
Thank you that makes sense. I appriciate all your help sir. Kind regards Mark |
This contribution was helpful to1 thankful Users |
Follow us on