Hello, You should import the GSD file of the EM277 into Step7. http://support.automation.siemens.com/WW/view/en/2615830 Assign it to the Profibus DP segment and configure the input/output module. Als configure the I/O offset in the V-memory (S7-200). At the S7-300 you communicate through the Inputs and Outputs assigned. And in the S7-200 you communicate through the V-memory Hope this will help. Wizard |