9/6/2022 4:42 AM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (873) |
Hello salah47, You always open topic in wrong conference. Your this post is related to Masterdrive VC & you posted it in MICROMASTER product conference mentioning it is MM drive. Please take care henceforth to atlest post in correct product conference. Now to your query, acceleration time in p462[001] = 0 is for FDS1, acceleration time p462[002] = 10 is for FDS2, & so on. Same for deceleration time i.e. p464[001] = 0 is for FDS1, p464[001] = 10 is for FDS 2. You need to check if FDS is activated in you project. To do so check status of Control word bit 16, & 17. Hope this helps. |
This contribution was helpful to1 thankful Users |