(1)| 3/12/2025 8:12 AM | |
Joined: 11/8/2020 Last visit: 8/8/2025 Posts: 6 Rating:
Hello! How to get rid of "no acknowledge" alams |
| 3/12/2025 8:53 AM | |
Joined: 1/21/2013 Last visit: 1/17/2026 Posts: 4405 Rating:
Hi Reinbergarne, The alarms you are complaining about are system diagnostic alarms generated within the PLC. If you do not want them to be reported to the HMI, you must uncheck the "System diagnostics" option under "Alarms > Controler alarms" in the Runtime Settings. Kind regards |
| 3/12/2025 12:54 PM | |
Didnt work. I changed my alarm class priority to 16 and scripted to show only those |
| 3/12/2025 1:53 PM | |
Hi Reinbergarne, You may need to reset the runtime values when you perform the download. Since the alarms are likely still active, they will not go away even if you disable them in the configuration. Kind regards |