(2)| 12/28/2014 8:44 PM | |
Joined: 1/28/2009 Last visit: 12/24/2025 Posts: 6885 Rating:
Hello juanjose, It is crystal clear from order number of CPUs and the versions , you have used the wrong set for a redundant system.For an H-system to enter the redundant mode, you need all modules in rack#0 and rack#1 to have same order numbers and same versions.So , please find same CPUs with "V4.4.0" /" V4.0.10" or update the firmware older CPU (or other option).More inforamtion can be found in getting started and updating firmware sections of the following manual:
SIMATIC Fault-tolerant systems S7-400H NOTE1:The manual explains the latest V6 products.
I hope this helps, Hamid Hosseini |
Last edited by: hdhosseini at: 12/28/2014 8:49 PMLast edited by: hdhosseini at: 12/28/2014 8:45 PM |
| 12/28/2014 11:02 PM | |
Posts: 5 Rating:
Correction: In the hardware the CPU version is diferent, but in online mode, from Component View, the version in both CPU is the same (V4.0.10) |
| 12/29/2014 6:58 PM | |
Posts: 5 Rating:
Send to you the file .zip whith diagnostic buffer
AttachmentDiagnose CPU Rack 1 29122014.zip (758 Downloads) |
| 11/8/2024 10:30 AM | |
Joined: 5/24/2022 Last visit: 5/21/2025 Posts: 2 Rating:
Dear Sir, I am facing same issue.. Your problem resolved or not ? If resolved how ? Kindly reply.. |