9/17/2024 6:51 PM | |
Joined: 9/16/2024 Last visit: 4/23/2025 Posts: 9 Rating:
|
Thank you for answering, It seems that we can only share one picture at the same time, so I attached a pdf with the software's real & declared configurations + the hardware configuration and comments. We are using Freelance as our software, and ABB AC800FR automats, mostly working with PROFIBUS DP nodes. AttachmentForum siemens 1709.pdf (596 Downloads) |
9/17/2024 7:55 PM | |
Joined: 9/21/2012 Last visit: 9/3/2025 Posts: 4702 Rating:
|
You have BusAddress 2 set to two different devices, that might be the problem source. |
9/19/2024 2:43 PM | |
Joined: 9/16/2024 Last visit: 4/23/2025 Posts: 9 Rating:
|
I guess that is what we are going to do, then. Thank you for your time |