Hello, Is it possible to configure the ET 200SP HA for I/O redundancy in TIA Portal when using a 1518HF PLC? |
12/4/2024 12:03 PM | |
Joined: 2/17/2020 Last visit: 8/29/2025 Posts: 1251 Rating:
|
Hi, I believe you can also use the LRedIO library (see below link) to connect the ET 200SP HA to a S7-1500H system: Connection of redundant I/O devices to S7-1500 Basically, if the IO-module offers a Value Status information, then the LRedIO library can be used. And this is the case with ET 200SP HA |
A rating will be well appreciated. |
|
This contribution was helpful to
1 thankful Users |
12/6/2024 9:04 AM | |
Joined: 7/8/2017 Last visit: 3/20/2025 Posts: 3 Rating:
|
Hi, As my understand The function for IO Redundancy (Hardware with terminal block M0/L0, M1) is not available in TIA V18, only can use in PCS7 and Step 7. As per Connection of redundant I/O devices to S7-1500, you also can use ET200SP-HA with S7-1500 with RedLib (seperated analog input module) Hopefully Siemens will have update can use in TIA in next update. |
Last edited by: viet_cong007 at: 12/06/2024 09:08:02 |
|