I have a redundant IM153-2 (CPU 417-H, ET200M). I originally used 6ES7 153-2AA02-0XB0. Two years ago, I replaced it with 6ES7 153-2BA02-0XBA0. The system has been working fine. But today, the right side IM153 BF1 is flashing slowly, the left side is working fine. So we replaced right side IM153. A new 6ES7 153-2BA02-0XBA0 was installed on the right side and the PROFIBUS connector. The problem still exists. Checking the error signal with pcs7, different order numbers were detected. Configured module: 6ES7 153-2AA00-0XB0, inserted module: 6ES7 153-2BA02- 0XBA0. 1.Why has it been running fine for 2 years but suddenly has problems? What went wrong? 2.If we don't want to change the hardware configuration settings and use 6ES7 153-2BA02-0XBA0, how can we do? Attachmentproblem.pdf (181 Downloads) |
Last edited by: kaoshihtang at: 01/26/2025 03:40:51Last edited by: kaoshihtang at: 01/26/2025 03:42:29Last edited by: kaoshihtang at: 01/26/2025 03:51:21 |
|
1/30/2025 6:10 AM | |
Joined: 2/16/2024 Last visit: 2/13/2025 Posts: 5 Rating:
|
We replaced 153-2AA02-0XB0 to 153-2BA02-0XB0 in January 2023, but we did not change the setting of HW Config R3~R7 Station (it is still 153-2AA02-0XB0). Until January 24, 2025, R3 Station has an error (the left IM153 module is normal, the right IM153 module BF1 Slow Flashing, BF2 Red light, Different order numbers detected). We have replaced the 153-2BA02-0XB0 module and Profibus connector, but the problem still exists. 1. Why has it been running fine for 2 years but suddenly has problems? What went wrong? (R4~R7 Station still work ok now) 2.If we don't want to change the hardware configuration settings (it maybe cause the device to become unavailable) and use 6ES7 153-2BA02-0XBA0, how can we do? Replace the IM153-2 backplane? Re-screenshot from simatic manager and make attachment as attached. Thanks for your reply. Attachmentproblem1.pdf (191 Downloads) |
Follow us on