Hi, I'm trying to use Modbus TCP to set the speed setpoint with another program, but I’m unable to write to the register I defined in the control logic. I suspect that “STW1.Bit10” might be causing the issue. Could you please guide me on how to set “STW1.Bit10 = TRUE” in Starter software? Best regards, Parviz ------------------------------------------------------------------------------------------ |
Last edited by: Moderator_Lan at: 03/03/2025 09:00:29New subject after splitting |
|
3/5/2025 12:14 PM | |
Joined: 10/11/2006 Last visit: 8/29/2025 Posts: 6037 Rating:
|
Dear TidalTurbine, the bit "control by PLC" (STW1.Bit10) can not be set with the Starter software. It must be set from an external control (for example a plc). Please find an example project under the following link: Please find a detailed description under the following link: |