Hi, Thank you for your reply Stefan, Please see in bellow |
5/21/2025 8:19 AM | |
Joined: 4/24/2006 Last visit: 7/31/2025 Posts: 9027 Rating:
|
Hello, Have you seen this link: Configuration of an HMI connection to S7-1500/S7-1200 CPUs Best regards, Wizard |
5/21/2025 8:41 AM | |
Joined: 4/17/2024 Last visit: 6/19/2025 Posts: 8 Rating:
|
Hi ,
yes , i have tried 1 and 2, none of them worked |
Last edited by: AutoGen_8733735 at: 05/21/2025 08:48:37 |
|
5/21/2025 9:24 AM | |
Joined: 4/24/2006 Last visit: 7/31/2025 Posts: 9027 Rating:
|
Hi, The message is about a Password Did you try it, recompile the project with the option "Rebuild All" and download hardware and software to CPU and HMI? And perhaps this link could help: How do I delete the IM folder of my TIA Portal project? Best regards, Wizard |
5/21/2025 9:53 AM | |
Joined: 4/17/2024 Last visit: 6/19/2025 Posts: 8 Rating:
|
Hi again, |
5/21/2025 10:07 AM | |
Joined: 4/24/2006 Last visit: 7/31/2025 Posts: 9027 Rating:
|
Hi, What is the online Firmware version of your CPU? Best regards, Wizard |
5/21/2025 10:27 AM | |
Joined: 4/17/2024 Last visit: 6/19/2025 Posts: 8 Rating:
|
4.0 |
5/21/2025 11:01 AM | |
Joined: 4/17/2024 Last visit: 6/19/2025 Posts: 8 Rating:
|
So, downgrade the firemware version to 3.0 in TIA Portal fixed the issue |