Here is the answer for your question: The concept of trip curves originated in the IEC world. The alphabetic code used to categorize miniature circuit breakers (B, C, D, K, and Z) was carried over from IEC standards. The standard defines the lower and upper thresholds for tripping, but manufacturers have the flexibility to decide the precise specifications within those thresholds that will cause a trip in their products. The trip curve graph shows the tolerance band within which manufacturers can set the individual tripping point of their breakers. Various tripping characteristics are therefore available for circuit-breakers, depending on the type of component or – B, C, and D for overcurrent protection of cables in accordance with IEC/EN 60898-1 – K for the protecting motors and transformers, and simultaneous overcurrent protection of cables with overload tripping based on IEC/EN 60947-2 – Z for control circuits with high impedances, voltage converter circuits, and semicable protection and simultaneous overcurrent protection of cables with overload tripping based on IEC/EN 60947-2. For more details, you can checkout this article: https://electgo.com/resources/mcb-trip-mcb-connection This articles includes the comparison for each type of mcb tripping curves |