mama ten sam problem co kolega , polacznie sie i odczytanie tejestru 30775 z sma nie działa , nawet jak wpisuje 430775 czy 30775 len2 status mam 8200, len0 , gdy zmienie len na 102 to status mam 7006 ------------------------------------------------------------------------------------------ |
Last edited by: Wit_Moderator at: 09/02/2025 12:21:47New subject after splitting |
|
9/2/2025 12:22 PM | |
Joined: 8/21/2014 Last visit: 9/5/2025 Posts: 1091 Rating:
|
Hello, U_10dcc3b0-14c1-4ee9-9c4b-ff40edaf6c80 Please try to discuss your question in English language. This is an internationalcommunityand we try to focus on one language. Posting in English will help you to get more response to your question. This is the translation of your question:
Best Regards, Wit_Moderator |
My Forum is the place to personalize your profile, |
|
9/2/2025 11:56 PM | |
Joined: 3/28/2010 Last visit: 9/4/2025 Posts: 1171 Rating:
|
1.Modbus activated? The manual "SMA andSunSpecModbus® Interface" located at https://files.sma.de/downloads/SMA-Modbus-general-TI-en-10.pdf states on page 20: 4 Configuration The two servers Modbus TCP and Modbus UDP are deactivated as default in the supported SMA products. You must activate the Modbus servers to use them. You can activate the Modbus ports of both Modbus protocols upon activation of the servers. Is the Modbus server activated and is the Modbus Port activated? I can't tell you how to activate, I've never heard of this device before, but Modbus communications can fail for numerous reasons, like inactive firmware or inactive port. Page 15 has information on Modbus Ports. 2. Register address You reference register 30775. Where did you find that register address? The manual above does not have a slave register list/map? Page 11 states that SMA supports both Holding and Input registers and it is critical that the master/client use the correct Function Code when polling the slave/server/ |