2/5/2016 8:55 AM | |
Posts: 1 Rating:
Hi, I am planning to use DDC controller and whether Siemens DDC will store 10,000 Events in the controller. Is it available ------------------------------------------------------------------------------------------ |
Last edited by: Blue Moderator at: 5/1/2016 8:27:54 PMNew subject after splitting |
2/16/2016 3:20 PM | |
Joined: 6/4/2010 Last visit: 9/30/2024 Posts: 387 Rating:
Dear Rammess,
The Desigo PXC50/100/200-E.D automation stations can support up to 4.000 BACnet objects each. All of them may have an alarm status.
Please note that the target should be to transfer the alarm and event messages to an alarm receiver instead of storing the alarm and events in the controllers. Storing the events locally is useless. The alarms and events should be sent immediately to a receiver, typically a Management Station for further processing. Desigo PXC50/100/200-E.D controllers have an alarm buffer size which can be adjusted. Default setting is 100, max. value is 500. This buffer is for situations where the alarm and event receiver is not online or not reachable. The alarms and events in the buffer will be transferred to the receiver as soon as the receiver in online again.
Please see the Desigo system description for further information: http://www.siemens.com/bt/file?soi=A6V10227660
or contact the local Siemens BT sales office which is
glad to help you.
Best regards, Albis |