5/20/2020 5:15 PM | |
Posts: 3 Rating: (0) |
Hi everyone, I need help reading a PT 100 with a RTD module. I did the parameterization but when I ran the program the value read from the input (Tag_11) was always 0. I changed the parameters and yet the value remained 0. I'm using the 4 wire sensor (below is the description). Any idea what the error could be? PLC: ET 200 Pro RTD Module: 6ES7 144- 4JF00 0AB0 AttachmentRTD_PT100.zip (413 Downloads) |
Last edited by: AutoGen_4913489 at: 05/20/2020 17:16:24 |
|
5/25/2020 10:46 AM | |
Posts: 3 Rating: (0) |
Hi all, I found the problem. In the input I have to use :P ... like %ID306:P |
5/27/2020 9:58 AM | |
Joined: 12/10/2018 Last visit: 6/27/2024 Posts: 109 Rating: (11) |
Hello dear Please read the attached file. It may be useful AttachmentET 200pro distributed I_O system.pdf (454 Downloads) |