Hi Krist, In practice it's never recommended to replace F-modules in running process because of the F-standards: Category 4 (EN 954-1)/ SIL3 (IEC61508)/PLE (ISO13849) Check the URL for wiring the F-AI: https://support.industry.siemens.com/cs/ww/en/view/24690377 Next if you have H-system then check in which OB's this Failsafe process is called and optimized. Check the wiring specifications of 6ES7 331-1KF02-0AB0/ 6ES7 331-1KF00-0AB0 modules and it's multifunctional options. Link attached below https://support.industry.siemens.com/cs/ww/en/view/8831413 https://support.industry.siemens.com/cs/ww/en/pv/6ES7331-1KF02-0AB0/td?dl=en Regards OmKris |