Hi
I prefer to control solenoid valves,using 4 F-DO module in conjuction with safety relays or 1 F-RO modules. It is more convenient to deal with common wire signal when you have volt free contacts.(also isolate load from DO module). Then you must watch out for the availability and reliability of the loop to meet your SIF requirements. As dear OMKRIS2017 said using external fuses for load circuits is necessary to protect relay contacts. Hope this helps |
Last edited by: hosein8419 at: 06/13/2021 00:43:13 |
|