Hello, Siemens has two types of S7-400 10A Power Supplies:
You should implement in HW configuration what is already installed in the system. I am sure that the installed type is 1st one while the configured one is the second. Thus because normally if you use the 2nd one (Redundant type) you should insert 2 power supplies (in slots 1&2 for 1st power supply and slots 3&4 for 2nd Power supply) and then insert the CPU. And that I didn't see in your pictures. Please have a look at the power supply itself and ensure with its part number and ensure that you inserted it correctly in HW configuration. Then download again and I believe the problem will be solved. Hope this helps. |
Ayman Elotaify |
|