5/3/2024 1:29 PM | |
Joined: 2/1/2010 Last visit: 7/17/2024 Posts: 149 Rating: (71) |
in TIA Selection Tool, make sure you have the newest version if using desktop version. Set the properties for the whole Rack from the main page and select without power bus. (working in desktop version) I didn't try online version with this feature. As for usage questions: 1. Nothing is required in HW config. 2.For using D-Sub, each module is automatically its own power bus, there is no option to use previous. Also if you are using the Siemens D-Sub base (e.g. H0) you have to supply power to the auxiliary terminals on the base. If you use the Phoenix D-Sub adapter that plugs into standard base (e.g. H1), you can use the auxiliary terminals or the power terminals at the Phoenix VIP terminal. The Siemens D-Sub does not connect the 24V through the D-Sub header, which is annoying. |
5/28/2024 8:26 AM | |
It is user preference. Your response and conclusion to the sales clarification seems contradictory to the actual requirements. Also I thought you just needed to know about software config not hardware requirements, sorry I could have included all this before. If you are going to use exclusively black terminal base or light gray terminal base, both of which requires new power group for each terminal, then you can use the CARRIER MODULE EIGHTFOLD (without PowerBus) 6DL1193-6GC00-8NN0 and save money since it is cheaper by about 30%. If you think you might ever mix and match dark gray terminals in any slots after a light gray to form a common power group, then you should use CARRIER MODULE EIGHTFOLD (with PowerBus) 6DL1193-6GC00-0NN0. |