Hi, you can use S7-1200 with 2 Ethernet Interfaces lik 1215C or 1217C or you check if the CP1243-1 fit your requirements |
6/8/2021 6:46 PM | |
Joined: 3/30/2020 Last visit: 9/26/2024 Posts: 4796 Rating: (984) |
Hello. The CPU1215 and CPU1217 do have two physical ports but those have the same IP address. The extension card is the better solution. A PN/PN coupler is second option. Routing the OPC-UA PLC through a network router is the third option. Setting overlapping subnets is the last option. Regards. |
Last edited by: qwazee at: 06/08/2021 18:57:35Activities of this user is voluntary. There is no obligation or liability placed on this user. Though optional, your 'please' and 'thank you' is highly valued. |
|
8/13/2024 6:33 AM | |
Joined: 5/16/2016 Last visit: 8/13/2024 Posts: 1 Rating: (0) |
SIEMENS support have other oppinion. |