Hi, Did you use "Project Migrator"? |
9/18/2024 9:39 AM | |
Joined: 8/3/2009 Last visit: 10/18/2024 Posts: 13982 Rating: (1760)
|
Hello AutoGen_3947755 first check this FAQ: https://support.industry.siemens.com/cs/ww/en/view/44029132 do you want to use the RT data of the old project? if no, reset Tag and Alarm logging and try again. try also to deactivate tag and alarmlogging in startuplist of the project first and have a look if this works. Have a look at the Logfiles in WinCC diagnose folder if there are any information about the statup crash Bye Murof |
Last edited by: Murof at: 09/18/2024 09:39:58If this Information really helps, you could use the Rate function |
|