Thanks for the clue Wuestenraeuber Dear Navnag, I meant that my modbus slaves/clients are still support modbus tcp/ip and not modbus RTU. I already have the CP341 for modbus RTU, the question was that: is it possible to use a protocol converter as an interface and if yes, whatthe difficulties are. |
11/25/2009 12:40 PM | |
Joined: 1/17/2007 Last visit: 10/15/2024 Posts: 1546 Rating: (537) |
The TCP / RTU convertor I have used in the past is one made by Lantronix. Lantronix Xpress-DR-IAP This will need loading with the modbus firmware (available from Lantronix website free of charge) before it can be used for modbus conversion. I have found the unit very easy to configure and it works very well. The serial interface can be RS232 or RS485. Hope this is helpful. |