Please can someone help in how to decode the diagnostic buffer error code e.g Requested OB: Programming error OB (OB121) Priority class: 1 Internal error, Incoming event 12:52:18.368 PM 02/27/2021 (Coding: 16# 2521 0179 8C74 0000 0022 0532) What is the meaning of each code which manual we can refer ? ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 03/03/2021 10:08:24New subject after splitting |
|
3/4/2021 3:07 AM | |
Joined: 9/1/2017 Last visit: 10/9/2024 Posts: 156 Rating: (19) |
Hi Bytes 1&2 : 2521 : event id (byte1:event class and identifier; Byte 2 : error code)--->2: synchronous error, 5: imcoming interal error, 21: BCD conversion error. Byte 3 : 01 : priority class of the ob where error occured. Byte 4 : 79 : OB number (ob121) Byte 5 : 8c : type of block where occured(8c means fc) Byte 6 : 74 : reserved ? Bytes 7&8 : 0000 :source of error (accumulator 1) Bytes 9&10 : 0022 : number of block where error occured Bytes 11&12 : 0532: relative address of command which error occured. System Software for S7-300/400 System and Standard Functions Volume 1 and Volume 2 Regards Hosein |