Joined: 4/28/2015 Last visit: 9/26/2024 Posts: 66 Rating: (4) |
On your opinion, command for the reading must be like here? |
5/18/2017 2:46 PM | |
Joined: 10/1/2013 Last visit: 5/8/2024 Posts: 605 Rating: (71)
|
But why are you trying to set 257.0 to TRUE? From my understanding 257.0 is a reserved bit. |
5/18/2017 3:00 PM | |
Joined: 4/28/2015 Last visit: 9/26/2024 Posts: 66 Rating: (4) |
I did a mistake with addressing and have finded this addiction |
5/18/2017 4:08 PM | |
Joined: 10/1/2013 Last visit: 5/8/2024 Posts: 605 Rating: (71)
|
Ah no problem. What about contacting the OMRON support? They should know about that behavior. I think I'm out of ideas. |
5/19/2017 11:26 AM | |
Joined: 4/28/2015 Last visit: 9/26/2024 Posts: 66 Rating: (4) |
Hello Qwei and all! I solved my problem. The trouble was in converting of addresses from siemens to Omron's tables of memory. For example, the bit READY is I257.0, the command EXE is Q257.0. I prepared picture with setings of TIA portal and converting of addresses, sorry for the big format of the picture. I hope it can be helpful for somebody. Manual for this RFID reader is on first message of this topic Also i made the sample project with CPU1511c and KTP600 Project v680s Omron - 1511c |
Last edited by: hadok at: 5/19/2017 11:34:43 AM |
|
This contribution was helpful to1 thankful Users |
11/6/2019 2:31 PM | |
Posts: 1 Rating: (0) |
Hi @Hadok Can you forward me your project ? I want to use OMRON V680S and i use TIA PORTAL V14. Please send me your project. Thank you. |