10/8/2015 6:02 PM | |
Joined: 3/30/2011 Last visit: 10/19/2024 Posts: 736 Rating: (256) |
Hello, F004 come because contactor doesn't close. Normally line contactor is closed by XR-109/110. The attached manual page show you what you need to close contactor. If something is not clear you can ask. Best RegardsAttachmentline_contactor.pdf (815 Downloads) |
Last edited by: mindware at: 10/8/2015 6:36:01 PM★★★★★★★★★★★★★★★★★★★★★★★★★★★★★★★★★★★★★★ |
|
10/10/2015 5:54 AM | |
Posts: 57 Rating: (0) |
Ok sir, i will recheck and confirm you |
10/25/2015 11:23 AM | |
Joined: 8/25/2006 Last visit: 10/18/2024 Posts: 2209 Rating: (279) |
Hello. After optimization of current controller you should run the optimization for speed controller (P051=26) and then optimization for field weakening (P051=27). Optimization run for compensation of friction moment and moment of inertia (P051=28) is not necessary for all drives, you should do it if it is required. |
10/27/2015 5:12 AM | |
Posts: 57 Rating: (0) |
ok sir. thanks. |