9/27/2023 2:05 PM | |
Joined: 3/27/2008 Last visit: 5/24/2024 Posts: 1106 Rating: (139) |
I may be misunderstanding this?? but can this be set by the ‘ramp’ time adjustment?? Tractor |
Tractor |
9/29/2023 5:01 AM | |
Joined: 3/25/2008 Last visit: 6/3/2024 Posts: 189 Rating: (8) |
Hello what kind of compressor are they? do they have any management?
10/15/2023 3:47 PM | |
Using the PI controller within the drive, this change you are referring to is a dynamic due to the performance of the system. If the PI controlling, and working, the rate of control required can only be managed empirically. As I look at my response it sounds like an excuse, but these things do take some time to set up, with a PC connected and using STARTER, sat on a packing crate trying to understand what is working or not? I have attached a drawing which may help, it refers to G120C for a Stairwell Pressurisation control system, but the parameters still apply to MM440 or MM430, and G120C. I hope this is a help with getting the response you require. Tractor
AttachmentG120C PID control.pptx (335 Downloads) |
Tractor |
This contribution was helpful to1 thankful Users |