Please check r047.002, .003 values whether any fault number is displayed in it. Please set P820.07 = 40 & check if the fault gets acknowledge. Please check supply voltages as below. CUD1 X174:2 & X174:1 = P10 X174:3 & X174:1 = N10 A2 card terminal XS 106 = 24 V DC. If above voltages are correct you need to either replace EEPROM C98043-A7009 or drive. Please read this FAQ for more information. 6RA70; SIMOREG DC-Master and CM; acknowledge fault message F040HTH |
1/10/2024 2:05 PM | |
Joined: 1/10/2024 Last visit: 1/10/2024 Posts: 1 Rating: (0) |
I´m solution. Clear and reprogram EEPROM of board C98043-A7009 |