5/25/2022 3:34 PM | |
Joined: 8/3/2009 Last visit: 11/19/2024 Posts: 14215 Rating: (1775)
|
Hello KevinS_Acieta The Accesspoint to load the Panel is blocked by the PLC Online Connection. You should go offline before you load the Panel. If you are connected with a VPN then the accessible device searching will not work (and also the setting with compatible devices). There are used DCP Broadcast packages and the most routers/firewals/gateways cannot do a DCP forwarding. so this will not work. You can try search devices with configured IP or use this FAQ: https://support.industry.siemens.com/cs/ww/en/view/109781206 Bye Murof |
If this Information really helps, you could use the Rate function |
|