Hi, I am also facing the same problem. i am using the V20 siemens vfd. the vfd is not tripping at overcurrent. I set the parameters P640 at motor full load(100%) and P 290 =1. I tried P640 with 50%. But the motor is not tripping at all. it is giving alarm of A501. but not tripping. can anyone help me for this? Thanks, Jaywant ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 04/18/2024 07:57:29New subject after splitting |
|
4/18/2024 8:02 AM | |
Joined: 3/25/2008 Last visit: 1/7/2025 Posts: 200 Rating: (8) |
hi P290 is a reaction to an overload of the inverter, not the motor |