9/2/2021 7:31 PM | |
Joined: 2/22/2008 Last visit: 2/22/2024 Posts: 2698 Rating: (206) |
See attachment for an other principle with counters and different weekday timers for the 2 shifts. You also can see the mappings for communication between the controllers. The counter values must be mapped separately, but i have used a logical VM area VM1xx and VM2xx for client and server. The VM1xx area of client is sent to the server at once, also all inputs of client, which are mapped to V1.x. V0.x is used, if you want weekday timers only in the client. But for this you need a stable network connection. Counter values greater than 32767 cannot be memorized directly, therefore i would prefer 2 weekday timers. Have a look to the Logo program and LWE project, wether this is the right direction or you need anything else. Of course the program is expandable, if you have details of your desired functions. Regard, Scorp AttachmentTime monitor.zip (328 Downloads) |
9/8/2021 10:07 PM | |
No answers to my questions ? That's not a good feedback for further help with the Logo program itself. Maybe there is no longer need for more informations on the monitor screen ? Sorry, but i have no step instructions for VPN connections, use the search function of the conference or google. One tip would be anydesk or onboard remote desktop functions for a PC to PC connection. Then you need a 24/7 running PC on the local side and any PC at remote side. I have used anydesk for home office during parademic lockdowns. Regards, Scorp |