Hello. I downloaded the Siemens application OIDCyclicExample. How do i monitor the communication to the MV550? For example there is a stop in communication, where do and how do I read that in the program to generate an alarm? Cheers |
6/8/2022 5:09 PM | |
Joined: 7/7/2010 Last visit: 4/26/2024 Posts: 14639 Rating: (2349)
With the diagnostics error interrupt interrupt OB, you are notified of new devices entering a problem state as well as when they enter a non-problem (everything is back to normal) state. You can also periodically poll the device for data that is always non-zero. You can add a parameter to your telegram for sign-of-life bit that toggles at a set frequency, then monitor it for either on or off longer than the toggle frequency. Lots of solutions available, but the most responsive is to accept the diagnostics error and handle it.
science guy |
This contribution was helpful to1 thankful Users |
6/8/2022 8:54 PM | |
Joined: 9/21/2012 Last visit: 4/27/2024 Posts: 3930 Rating: (444) |
DeviceStates is a nice instruction, to poll devices. |
6/9/2022 9:48 AM | |
Or rather 257? Looks more logic when i read documentation. |