Hello: I have experienced exactly the same problem. Every time I try to connect a TCP Modbus client (Modscan32) to my LOGO, this terminates the TCP/IP connection inmediatelly. Any idea about the issue? I am only trying to read the I/O. Nothing found in other threads. I am able to connect the same Modbus client to other devices. Thanks and regards ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 05/29/2019 13:33:24New subject after splitting |
|
5/29/2019 12:50 PM | |
Posts: 3 Rating: (1) |
I answer myself! The default TCP port is 510!!! (instead of 502). Now the Modbus TCP commmunication is working ok. Regards |
5/30/2019 12:32 PM | |
Posts: 3093 Rating: (323) |
Hello, Regards, |
1/21/2023 2:10 PM | |
Joined: 12/18/2014 Last visit: 11/18/2024 Posts: 34239 Rating: (4263)
|
LOGO! reserves ports 502 to 509 for the 8 static Modbus server connections on Modbus. |