Hello Experts, We need to work on WinccOA 3.10 on a old system around 12 years. The system has redundant systems. 1) Need to take backup, Can u suggest steps to take backup, Only copying files is sufficent. 2) Add some Modbus TCP tags (read/write), Which software to access the settings... 3) Any synchronisation process after development. We tried searching the web but 3.10 material is difficult to be seen. Thanks in advance. ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 06/19/2023 10:01:16New subject after splitting |
|
6/21/2023 7:18 AM | |
Joined: 6/23/2013 Last visit: 10/1/2024 Posts: 63 Rating: (6) |
1) If the project is stopped then copying the files is sufficient. Otherwise the online backup tool has be used to backup the database (db directory) 2) The gedi is the tool for engineering 3) There is nothing to synchronize, development is done on a running system |
WinCC OA expert |
|
6/23/2023 7:31 AM | |
Joined: 6/14/2023 Last visit: 10/1/2024 Posts: 2 Rating: (0) |
Hello Gertjan, Thanks for your response, As seen in the system it has following folders Siemens Automation\ Runtime Systems \ WinCC OA 3.10 \ ......Console, De-Installation, Help and Project Administration. Gedi is not available anywhere. Any specific location where should I look into ? May be the tool for engineering is not installed. Can I download it from Siemens website or any other location. Also its 3.10 so will it be fine to use the latest version (3.19) and put back the updated files. I copied the project folder around 9.8 GB. Best Regards |
6/27/2023 6:27 AM | |
Joined: 6/23/2013 Last visit: 10/1/2024 Posts: 63 Rating: (6) |
The gedi is built in the standard user interface, but started with a different option '-m gedi'. You could go thru the getting started to get some knowledge about the basics in case you cannot attend a basic training. |