3/25/2012 7:46 AM | |
Joined: 4/14/2010 Last visit: 8/6/2024 Posts: 525 Rating: (11) |
Greeting, Could you please describe the what will pin configuration for Communication Cable Between Siemens MP277 8" touch & Allen Bradley SLC5/03 Proccessor with DF1_DH485. can i use attached pin configuration..??? Or any Order Number...?? Thanks, Regarded. Attachmenthmi cable slc500.pdf (303 Downloads) |
Last edited by: Sarfraz Bhatti at: 3/25/2012 8:58 AMMS |
|
3/26/2012 7:36 AM | |
Joined: 9/28/2005 Last visit: 11/5/2024 Posts: 2957 Rating: (242)
|
Hi, MP277 has one port RS485, one port RS422 and one ethernet port. So the attached cable is not good for you. Does your PLC has RS485 port ? You need to use it. Also maybe you can use RS232/485 converter, but I'm not sure if it will work. Also look here SIMATIC HMI WinCC flexible 2008 Communication Part 2 chapter 2. |
Best regards, |
|
3/26/2012 2:52 PM | |
Joined: 4/14/2010 Last visit: 8/6/2024 Posts: 525 Rating: (11) |
Many thanks for reply Darius, MP277 6AV6643-0CB01-1AX1 has only one DB 9 port we can select our protocole via Dip switch RS422/485. We can use SLC500 with DF1 or DH485 via Siemens IF1B RS422/485 Selection have a look attached Wincc flexible connection for Allen Bradley SLC PLC. We need pin configuration for this protocole or any Siemens_AB cable order number..??? My question Can i use AB cable 1747-CP3 wich is mentioned in Wincc flexible manual part2 see attached...?? Thanks, Regarded. AttachmentDesktop.zip (197 Downloads) |
MS |
|
3/28/2012 11:16 AM | |
Posts: 3037 Rating: (192)
|
Hello, |