5/24/2012 3:18 AM | |
Joined: 1/3/2006 Last visit: 2/19/2024 Posts: 726 Rating:
Hello, Please perform OS update and see. |
5/25/2012 1:09 PM | |
Posts: 3037 Rating:
Hello, Do you use logs in your project? Then you must close the runtime on your panelwith the function "StopRuntime". The runtime is down, then you can switch off the panel. If you switch off the panel without shutdown of the runtime withthe function "StopRuntime", the logs could be faultily. See the first note in the chapter 1 in the following FAQ. How are tags and alarms logged in WinCC flexible? Tweety |
5/29/2012 10:25 AM | |
Posts: 3037 Rating:
Hello, You have a possibility to repair defect logs onyour storage card. You mustenable the option "Automatically repair file system errors on storage cards at system startup and card insertion time" on your MP277. You find this option on your MP277 under "Control Panel > OP > Persistent Storage". Then you reboot your MP277. The logs are repaired automatically at the restart. You can see this option in the following FAQ in picture 1. Which external storage locations are available on the various operator panels (TIA Portal/WinCC flexible/ProTool) for archiving data? Tweety |
7/14/2012 9:58 AM | |
Posts: 5 Rating:
Thanks all I used card reader to delete the corupt file & everything is OK. |