11/25/2012 11:03 AM | |
Posts: 42 Rating: (2) |
Hello everyone. I've to program a simatic panel TP177B - siemens code 6AV6642-0BC01-1AX1. I'm using Wincc Flexible 2008 SP3, but when I try to add a new panel, i cant see it. In the list there's only TP177B mono, and TP177B color PN/DP As i can see from theTechincalDatathere's no PN interface in this model, but colors says "Blue Level" Unfortunately i havent that panel here to test, it's already in the plant of the customer. Maybe i cant program it with 2008 SP3 and i need an older version? Maybe the PN/DP one is compatible with my panel? I would like to avoid problem during the commissioning.. Any suggestions? Thank to all anyway
|
11/25/2012 11:50 AM | |
Joined: 8/31/2010 Last visit: 11/6/2024 Posts: 1523 Rating: (229) |
Hello suppaman87, You can choose the HMI as "TP 177B mono DP". Do not worry, you can use WinCC Flexible 2008 SP3 for the panel which u have at site. You need not do any modifications when you download the project to the Panel at site. |