Haveyou checked to connect both of them in to two differenct modules? Please revert back after trying this.. |
6/26/2013 8:23 PM | |
Joined: 4/20/2007 Last visit: 5/27/2024 Posts: 724 Rating: (42) |
does the FO supply 24 VDC? if so is your Ai set to 4 wire? if not, set it to 2 wire.. |
6/27/2013 1:30 AM | |
Posts: 72 Rating: (6) |
Have you measured the current coming properly from drive? Check it out with multi meter while connecting it with PLC.
|