Hello Adil; The best document for this type of information is the Standard and system functions manual for S7-300 and S7-400 CPUs. Like a lot of documents available from Siemens they are presented in various languages, to allow programmers form different backgrounds to look at the information. Here are links to the French and English version: SIMATIC Logiciel système pour SIMATIC S7-300/400 - Fonctions standard et fonctions système - Volume ½ https://support.industry.siemens.com/cs/ww/fr/view/109751826 SIMATIC System Software for S7-300/400 System and Standard Functions - Volume ½ https://support.industry.siemens.com/cs/ww/en/view/109751826 The screenshot below shows the interpretation of Event ID #16 #530D. It is not really helpful , since it points to a restart operation of the CPU. To understand why the CPU needed to restart, we need the full diagnostic buffer (as a text file, use the Save AS.. button on the diagnostic buffer page) as suggested earlier by our friend ixo65. Hope this helps, Daniel Chartier |